Hi pros,
I was programming 2 UR10, and one of theme use digitals I/O.
The problem here, is that all outputs stay at high level and I can't bring theme down.
If I touch an output it go low for around 0.1 second before go back at high level.
I've tried to force the outputs to low levels using the installation tab and choosing the "low when not running" parameter on all outputs. With this parameters up, we can see that something is trying to put the outputs at high level just before the parameter bring them down.
I've disconnected the 2-finger gripper (USB + alim), the network between the 2 UR, and every thing on I/O ports.
The 2 UR10 are on CB3.1 and up to date.
Here a short movie with the I/O tab : https://www.dropbox.com/s/slj8vhkblutwlhk/IMG_2358%5B1%5D.MOV?dl=0
Thanks for your responses.
Best Answer
-
PierreDenis Posts: 4 Apprentice
I've solved my problem! Thanks to Loïc who is a DoF community member too.
The problem is that I was using the port 1 on the Modbus, which is normally used to set the outputs, so this was effectively my Modbus which was putting all my outputs up.
Thanks to Loïc I know now that I can use a port between 128 and 255 without any problems. All the other ones are reserved for something else.
So, if someone use the address of the UR to communicate with it, remember to use a port between 128 and 255 in order to avoid any problem.
One more ore dumb question....have you tried rebooting the robot?
Hi,
All I/O blocks are removed but the problem is still here, like you can see in this short movie : https://www.dropbox.com/s/4f9jfeogdzflb34/IMG_2359.MOV?dl=0
I've made my short program following these few steps, and I've made tests between each of them:
- made a simple move -> OK
- add I/O -> OK
- add ModBus -> NOK
I'll try to restart from the beginning but I'll add ModBus before I/O.
And Yes I've reboot the robots, they where OFF for 2 days. When I try them this morning the problem was still here.
I'm also in touch with a technical support, but for now, no solutions have been found.
I've just remade my program:
I've start with a simple move from pointA to pointB -> no problem
When I add a line in the before start section to put "255" on Modbus. The outputs start to blink (because they have still the parameter that forced them à low level when the program is not running)
So I see here that the Modbus have effect on outputs for no reasons. And of course the Ethernet is not connected to the UR....
https://www.universal-robots.com/how-tos-and-faqs/how-to/ur-how-tos/modbus-server-16377/
These can be really handy, especially when you have multiple robots in a cell as one robot can see what the status of the inputs are on another one. Very handy when you have more I/O on one robot than you have capacity built-in and another with excess I/O. They can effectively use each other as modbus expansion systems.